However, several UL designs used the pre-2006 WSD Method—where structural members were tested with lower loads than those called for by the LSD or post-2006 WSD methods. Thus, according to UL, assemblies tested using the latter methods would have a shorter fire-endurance period. To address this discrepancy, load restrictions are imposed on UL designs evaluated under the pre-2006 WSD method, as stated in the disclosure at the front of the design:

design method other than the Limit States Design Method (e.g., Working whatsapp number database Stress Design Method). For jurisdictions employing the Limit States Design Method, such as Canada, a load restriction factor shall be used – See Guide BXUV

The above disclosure states “for jurisdiction employing the Limit States Design Method,” when in fact, a more appropriate statement is “for projects employing the Limit States Design Method.” The design method is, in fact, the choice of the project team. While the US does not mandate the use of the LSD Method as Canada does—it is widely used throughout the US design community. Even if the post-2006 WSD Method is used, the result is the same.